Author Topic: COMM1 pinout  (Read 10566 times)

vsingh

  • Newbie
  • Posts: 6
    • View Profile
COMM1 pinout
« on: October 02, 2004, 11:52:25 AM »
I know that COMM1 on MX1616+ has only three documented pins. Are the other pins on the connected or are they connected to power and ground in some undocumented manner ?

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:COMM1 pinout
« Reply #1 on: October 02, 2004, 03:34:47 PM »
Only pin 2,3 and 5 are used on the T100MD+ PLC. T100MX+ PLC uses pin 4 to get power from the host for its opto-isolated serial interface so pin 4 is also required.

For T100md+, all other pins are not connected to power or ground. Pin 1,4,6 are shorted on board and pin 7 and 8 are shorted on board. These are to provide loop backs for the RTS/CTS pair and DTR/DSR if you use a 9 wire conductor. These signals are not used by the PLC but some host computer/modem etc may want to see these signal being looped back in order to allow communication to take place.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS