Author Topic: Timers won't turn off  (Read 26496 times)

Carolyn

  • Guest
Timers won't turn off
« on: December 16, 2003, 07:19:54 AM »
I'm trying to use a timer to increment a sequencer.  Basically, I have step 2 of Sequencer 6 energize a 5 second timer.  Once the timer is on, it will set Sequencer 6 to step 3, at which point the timer should turn off because power is no longer at step 2 of the sequencer.  In the simulation, however, the timer coil stays on and will not turn off.  Does anyone have a possible explanation for this?  I have a screen shot of the circuits, but I couldn't figure out how to post that here.  Thanks!
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3182
    • View Profile
    • Internet Programmable PLCs
Re: Timers won't turn off
« Reply #1 on: December 16, 2003, 12:06:33 PM »
Try moving the rung that contains the timer coil to the further down the ladder rung from the sequencer. The reason is explained in Page A 1-3 of the Internet TRiLOGI Programmer's reference under the topics "3. Timer Contact Updating Process".

If this does not resolve your problem, your can email your program to support@tri-plc.com with explanation note on the problem area and we will examine your program and identify the problem in your codes.
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS