Internet PLC Forum
General => Technical support => Topic started by: Carolyn on December 16, 2003, 07:19:54 AM
-
I'm trying to use a timer to increment a sequencer. Basically, I have step 2 of Sequencer 6 energize a 5 second timer. Once the timer is on, it will set Sequencer 6 to step 3, at which point the timer should turn off because power is no longer at step 2 of the sequencer. In the simulation, however, the timer coil stays on and will not turn off. Does anyone have a possible explanation for this? I have a screen shot of the circuits, but I couldn't figure out how to post that here. Thanks!
-
Try moving the rung that contains the timer coil to the further down the ladder rung from the sequencer. The reason is explained in Page A 1-3 of the Internet TRiLOGI Programmer's reference under the topics "3. Timer Contact Updating Process".
If this does not resolve your problem, your can email your program to support@tri-plc.com with explanation note on the problem area and we will examine your program and identify the problem in your codes.