I have made the measurements as you said and it is
150mV (milli volts), give or take 5mV AC. On DC setting
it is 0Volts to three decimal places. The measurement was
between pin 5 of my PCs serial port to the ground terminal
of the PLCs power supply. I have also made a similar
measurement to a serial port of another PC and got same
results.
I had the PLC powered up and connected to the PC for
several days while I was reading up on the manuals to
educate myself. I had reset the RTC many times to clear the
RTC error alarm.. There was no indication of any problem at
any of these times. I did not see any problem until I did
a program transfer to the PLC; that I do not understand.
Shouldn't the grounding problem have affected the PLC even
before I did the program transfer?
I would be glad to try another power supply if you can tel
me who the supplier is for power supply you mentioned. I am
willing to try everything and anything to get this project done.
thank you for taking the time to help.