Multi inputs controling 1 relay
« on: December 09, 2008, 12:08:22 PM »
could someone please help me with some lader programming.
here is what I want. I have 6 inputs when any input is tripped I want relay 1 to close for 5 sec. ( I got this part working ok ) here is the problem. If any one or more than 1 input latches I still need relay 1 to trip for the 5 sec if there is an input from any other input that isn't latched, and once the latched inputs clear I will need to be able to have it all start over again. This is for a E10+ and I am useing TRiLOGI ver. 3.53 Thanks for any help, an example would be great.  ;D

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Multi inputs controling 1 relay
« Reply #1 on: December 09, 2008, 08:23:47 PM »
If any of the input turns on, trigger a [DIFU] relay and use it to reset the latch that you used to activitate the timer. That way a new input would cause the timer to run again.