Technical support / Fx2424 PLC backwards compatible with T100MD2424
« on: December 09, 2019, 01:30:14 PM »
Hi,

Is the Fx2424 PLC backwards compatible with T100MD2424? I have had a bunch on inputs (including high speed counters) fail on an old T100MD2424 and was looking to replace with a Fx2424 but don't want to have to reinvent the wheel, reprogramme, commission, etc.

Thanks

2
Technical support / Re:FMD88 D/A#3 and D/A#4
« on: February 12, 2017, 11:01:37 PM »
I have my head around this now. 4095 is 12bit resolution but I now remember that the T100MD had 10 bit but the plc firmware scaled it to a 12 bit equivalent. So this is why I don't have a problem between PLC versions.

Still don't know about the wiring though.

3
Technical support / Re:FMD88 D/A#3 and D/A#4
« on: February 12, 2017, 10:44:46 PM »
Thanks Gary. Now I'm really confused as I have used these PLC's a lot and haven't changed any of my software between changing from T100MD to FMD88 and the analogues have always read fine in my SCADA with a max scale of 4095?

Regarding the wiring, the only difference with the way I have the connections configured is that the pins allocated "future #D/A3 and #D/A4" are connected to 0V all other pins (apart from A/D#1-4) are not connected.

4
Technical support / Re:Resin encapsulation?
« on: February 12, 2017, 10:32:19 PM »
Thanks for the answer.

5
Technical support / FMD88 D/A#3 and D/A#4
« on: February 11, 2017, 02:09:47 PM »
Hi, I have had to swap an old T100MD888 with a new FMD88 but had an issue with the analogue input values I was reading. From what I can see from the connection wiring the only difference is that our application connects the future D/A's #3 and #4(pins 10 and 11)  to 0V as that is what these pins were on the T100MD888.

Would this be the cause of the spurious analogue input readings I now get? If not, are there other differences (software and hardware) that I should be made aware of when swapping a MD888 with a FMD88?

Thanks.

6
Technical support / Re:Resin encapsulation?
« on: February 11, 2017, 02:03:43 PM »
Revisiting an old thread again...but this has recently become an issue for me and I realize that I never got an answer to the question regarding application of a lacquer.

7
Technical support / DO Issue
« on: July 11, 2016, 01:27:06 AM »
Hi,

I have a FMD88-10 (Rev 3) which is showing something unusual. Digital outputs 1-4 aren't working correctly and when energised in the code, they don't turn on (sometimes they flicker) but the RTC error light flickers.

Any ideas what the cause may be?

Thanks

8
Technical support / Re:Resin encapsulation?
« on: October 16, 2015, 02:17:42 PM »
I am using MODBUS RTU with error checking. In the case of a communications error the SCADA values are not overwritten so I am confident that the analogue drop outs are not coms related.

9
Technical support / Re:Resin encapsulation?
« on: October 14, 2015, 11:19:40 PM »
The PLC's are polled at 10 minute intervals so it is hard to know how intermittent the fault is. I haven't seen the values at 0 for longer than one poll. When the error happens all inputs fall to 0.

10
Technical support / Re:Resin encapsulation?
« on: October 13, 2015, 12:04:26 AM »
Reviving an old post here but I am having an issue with a couple of installations where we see our analogue inputs randomly and intermittently dropping to 0 on FM88 PLC's. These seem to occur when there is a chance of high humidity and potentially condensation in the cabinet, which we obviously try to avoid. To try and prevent this from happening I was looking at using a lacquer spray like the one linked below to coat both sides of the PLC.

Can you confirm whether this is OK to use and whether there are any components we should cover before spraying? I'm not too worried about issues around being able to replace components as we haven't had to do that for a very long time.

http://www.jaycar.co.nz/Service-Aids/Chemical-Aids/Aerosols/Circuit-Board-Lacquer-Spray-Can/p/NA1002
 

11
Technical support / Re:Output Fail
« on: May 04, 2015, 12:55:18 AM »
I am using DAQFactory and I am sure that there is no way that the SCADA can falsely show status as the screen display is directly mapped from the MODBUS reading from the PLC.

I was monitoring the status with Trilogi but unfortunately can't remember what it showed and I haven't been able to repeat the error since.

12
Technical support / Re:Output Fail
« on: April 29, 2015, 11:56:30 PM »
All of the outputs showed the fault.

I didn't take note of the 3 LED's apart from noticing that the RTC Fault LED didn't turn on so it does sound like a hardware issue to me.

13
Technical support / Output Fail
« on: April 28, 2015, 11:33:49 PM »
I have had a situation with an FMD88 where I could still communicate via ethernet and monitor the status of inputs but when I tried to activate outputs through my SCADA interface, the physical outputs didn't turn on but the status read back from the PLC showed that they were activate. This would imply that the code was still functioning as there is logic that maps SCADA commands to outputs but the physical outputs didn't trigger.

I re-powered the PLC multiple times and it made no difference. After leaving the PLC off for 30 minutes or so and turning back on again, it seems to be functioning correctly. I have not been able to replicate the issue since.

I can't say for sure but I don't think the RTC Error light was on while I had the problem. Any ideas?

14
Technical support / Maximum PLC ID for Modbus RTU
« on: August 01, 2014, 04:42:34 PM »
I remember reading before that the PLC ID's were only valid up to a limit when using MODBUS RTU. I can't find this reference anymore, could you please confirm what this?

Thanks

15
Technical support / Re:RF Noise
« on: May 26, 2014, 01:30:31 AM »
Well it has been a while but I can now provide an update.

Gary: if you are still there, the RF chokes helped but didn't solve the problem.

Support: you were right. After a lot of trial and error testing we found the noise to be coming from the switch mode DC-DC converter. It wasn't that easy to find and we were mislead by the fact that unplugging the PLC made the noise go away...this still isn't really explained. Perhaps the noise from the DC-DC converter is load dependent (i.e., PLC small load is enough) or perhaps there is an interaction between the two that amplifies the noise to the radio.