Technical support / Re: NANO-10 and Weintek MT8050iE 4.3" Touch panel
« on: August 15, 2022, 11:52:49 AM »
Neal,
The simplest way to have all three devices connected simultaneously is to use Modbus RTU over the RS485 port for your TX4S as you had been doing, and then connect the HMI to the PLC via Ethernet.
The Nano-10 and MT8050iE can be connected directly via Ethernet or through a switch. I assume you are programming the Nano over Ethernet, so you would need a switch in order to have both the PC and HMI communicating with the Nano.
Using the TRi_Fx driver, you should be able to communicate via Ethernet. Alternatively, you can use the Modbus TCP driver provided by Weintek.