Author Topic: Counters  (Read 5381 times)

Alex

  • Newbie
  • Posts: 1
  • I'm a llama!
    • View Profile
Counters
« on: August 04, 2006, 10:56:47 AM »


Hi,

I need to count objects increment/decrement fastly and I have to use inductive sensors and I need to use the HSC1 but it works only with encoders, whant can I do?

Thank you

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3171
    • View Profile
    • Internet Programmable PLCs
Re:Counters
« Reply #1 on: August 04, 2006, 03:22:38 PM »
If you leave input #4 OFF and only feed the pulse to input #3, then by default it is a single-phase high speed counter and should be able to count your pulses up to 10,000 pps. Do not execute the SETSYSTEM command to put it in enhanced quadrature mode if you want to use it as single phase high speed counter.