Today while operating the plant, the TM100MD2424 #1 output began acting very strange, when #1 output was told to turn on, all of the other outputs began switching on and off at a high freq. I changed the omron relay connected to #1 output and this solved the problem. Could this have been due to a failed or shorted omron relay, or is this a function of the PLC hardware?