T100MX+ and T100MD+ support both MODBUS ASCII and RTU PLCs. But earlier generation of the M-series PLC (those without the plus sign on their CPU, and firmware revision is below r30) DO NOT support RTU mode, only ASCII mode. Is your PLC an earlier model? If so, then you can only use the ASCII protocol. The MODBUS ASCII protocol works well for all the M-series PLCs.