Author Topic: Master Reset of Slave PLC  (Read 12568 times)

montyk

  • Newbie
  • Posts: 11
    • View Profile
Master Reset of Slave PLC
« on: August 20, 2008, 07:32:11 AM »
I am using an MD2424 as a master controller and using it to set  and read varibles in eight MD888, using the hostlink commands with a RS485 loop and then they control the processes. But I have run in to a porblem were on of the slave MD888 will get bad data loaded into a varible which causes it's program to pause because of a data out of range alarm, if I reset the unit it starts to run again. Is there a command that the Master controller can send to the slave to cause a Master Reset in the slave unit when it can not communicate with the slave unit.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Master Reset of Slave PLC
« Reply #1 on: August 20, 2008, 02:58:32 PM »
You can send the "CL" command to the slave to reset it.

Alternatively, in the slave PLC, add a circuit as follow:
      RLY1
|-----||---------------[MaRST]

This way you can turn on RLY1 in the slave to cause it to reset itself.