Author Topic: PLC and Appliance connection - Need Help  (Read 5341 times)

nheilBRO

  • Newbie
  • Posts: 17
  • I'm a llama!
    • View Profile
PLC and Appliance connection - Need Help
« on: June 17, 2006, 06:13:03 AM »
Hi All,

I am a newbee in this electronics gadget, I have T100MD888+ that I want to connect to a cannivalized CPU cooling fan, I cannot figure out how this things works. Anybody could give guidance< I will appreciate it.  thank a LOT.

Btw.

I am using TriLOGI 5.xxx for Lodder Logic Design.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3171
    • View Profile
    • Internet Programmable PLCs
Re:PLC and Appliance connection - Need Help
« Reply #1 on: June 18, 2006, 01:59:53 PM »
What is the voltage rating of the cooling fan?

If you use the T100MD888+ with 12VDC you can connect "+" end of the fan wire to +12V, the "-" end goes to PLC's output and it will work with any output.

If your PLC runs at 24V, then you can only use the PLC output #7 or #8 (as PWM output) and set duty cycle not more than 50%. You can change the duty cycle to vary the fan speed. The average voltage applied to the fan at 50% duty cycle = 24 x 0.5 = 12V DC.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

nheilBRO

  • Newbie
  • Posts: 17
  • I'm a llama!
    • View Profile
Re:PLC and Appliance connection - Need Help
« Reply #2 on: June 18, 2006, 06:04:02 PM »
thank for the advice.
I will contineu my experiment.

Btw.

the voltage of the cooling fan is 12v.