Author Topic: Minimum Enclosure for PLC  (Read 10310 times)

Roger Shaffer

  • Guest
Minimum Enclosure for PLC
« on: December 29, 2005, 03:03:55 PM »
I was just wondering what the minimum enclosure size for your MD888 series PLC?  I was considering using an aluminum enclosure without venting.  

Your recommendations are greatly appreciated.

Thank you

plcuser

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3176
    • View Profile
    • Internet Programmable PLCs
Re:Minimum Enclosure for PLC
« Reply #1 on: December 29, 2005, 04:43:09 PM »
A lot of factors can affect how the heat can be transferred from inside a sealed enclosure to the environment. This include the environmental temperature of operation, the conductivity of the box, the airflow outside the box etc and really there is no simple rule of thumb to say how big a box should be used. Probably the bigger the better.

If you can use the PLC at lower operating voltage (say 12V DC) then heat dissipation will not be a problem and you can use as small a box as can contain the entire PLC without touching any conductor.

If you are running at 24VDC then you have to prevent the internal temperature of the box from exceeding the maximum temperature. The alumnium box is good heat conductor but the internal volume  of the box should allow heat convection and there should be adequate airflow outside the aluminium box.
« Last Edit: December 29, 2005, 10:06:16 PM by support »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS