I need read 2 rtd (pt100) sensor with T100MD888+PLC, please give me any sugestion.

Thank alot
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3180
    • View Profile
    • Internet Programmable PLCs
Re: rtd (PT100 sensor)
« Reply #1 on: November 17, 2002, 07:23:07 AM »
The quickest means is to buy a commercial PT100 signal conditioner that will output 0-5V, 0-20mA or 0-20mA (the latter two can be converted into voltage by using a 250 ohm resistor) and connect to the T100MD888+'s analog input.

You can also build a two-resistor voltage divider using the PT100 as one of the resistors and construct a simple opAmp to amplify the voltage drop across the PT100 resistance into 0-5V.  A sample circuit can be found at the following link:

http://www.tri-plc.com/applications/PT100Interface.pdf


« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

rosssyscon

  • Newbie
  • Posts: 6
  • Thanks for the help!
    • View Profile
Re: rtd
« Reply #2 on: September 10, 2003, 04:04:42 AM »
We just hooked up an RTD using the diagram from page 6 of the installation guide. Rather than a 1K Ohm Pot, we have a 100 Ohm RTD. (Using T100MD-1616+)

So far it works just fine. This allows us to bypass the expensive converter. Are there any problems with this? Are we going to experience problems later?
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3180
    • View Profile
    • Internet Programmable PLCs
Re: rtd
« Reply #3 on: September 10, 2003, 11:00:09 AM »
I assume you are using the RTD in series with a resistor to provide the voltage dividing effect as outlined in the document:

http://www.tri-plc.com/applications/PT100Interface.pdf

The only thing you need to check may be whether self-heating of the RTD may affect the readings slightly, but there should not be any long term ill effect on the connection.