Analog output scale
« on: April 27, 2005, 11:39:57 PM »
Hello,
   I have T100MX-3224R but analog  output  just 0-2V (pin 9 and pin 13 of DB15  ) How can i adjust it ? (0-5V)
   

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Analog output scale
« Reply #1 on: April 27, 2005, 11:58:31 PM »
Unlike T100MD+ PLC which outputs a +5V on pin 13-15 and 0V on pin 9-11, the T100MX3224R require an external +5V DC analog voltage reference to by applied to the AVcc and AGND inputs.  i.e. You have to find a good stable analog power source +5V to be applied to the analog reference terminal. Take note that connecting a wrong voltage to the AVCC and AGND will instantly kill the CPU so be careful.