Author Topic: RS232 on Nano-10  (Read 5105 times)

kparson

  • Newbie
  • Posts: 5
    • View Profile
RS232 on Nano-10
« on: December 15, 2011, 02:25:23 PM »
Is there a simple and inexpensive way to convert the Ethernet port on the Nano-10 to RS-232?

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3171
    • View Profile
    • Internet Programmable PLCs
Re:RS232 on Nano-10
« Reply #1 on: December 16, 2011, 08:21:05 AM »
Ethernet and RS232 are very different in nature so there is no simple conversion. But it is very easy to convert the RS485 of the Nano-10 into RS232 port using the Auto485 (http://www.tri-plc.com/auto485.htm)

However, unless size is a problem, it probably make more sense to get the FMD88-10 which has both RS232 and RS485 ports built-in.

But if your purpose is to use the Nano-10 as a Modbus/TCP to Modbus RTU Gateway, then the new Nano-10 can be configured to act as a Modbus Gateway, where any Modbus/TCP with ID that is not the PLC's ID will be sent out and received using Modbus RTU protocol via the RS485 port to other Modbus slaves. That is a new feature on our Nano-10, FMD or F-series PLC with r77 or later firmware. Contact support@tri-plc.com if need the specific instruction to enable the Modbus gateway mode.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS