Author Topic: Dead RS485 Nano Display  (Read 12213 times)

raan

  • Newbie
  • Posts: 31
    • View Profile
Dead RS485 Nano Display
« on: March 03, 2011, 12:12:11 PM »
I have a nano 10 with the rs485 display and due to the use of two voltages 24vdc and 60vdc in the circuit (motor supply and plc supply) and a disconnect switch in the negative common lead I some how managed to cause the display to stop reading when I opened the disconnect possibly back feeding voltage to the display. The PLC is still functioning okay. I changed  out the rs 485 ICs hvd3082 8 pin dips in the controller and in the display but to no avail. Any suggestions ?

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Dead RS485 Nano Display
« Reply #1 on: March 03, 2011, 05:18:14 PM »
When you power on the MDS100-BW, does the LCD backlight comes on and does it show any start up message and report the ID? If so then the LCD display is still good and the CPU on the MDS100-BW appear to be working and the problem may only be limited to the RS485.

Since you have the Nano-10 I assume you have the U-485 adapter? If so, you can try to use TLServer to communicate with both the Nano-10 and the MDS100-BW to see if you are to able to communicate with both devices via their RS485 port. To communicate with the MDS100-BW you need to know its ID (default is F0 unless you have changed it) and then send the correctly formatted command string with correct FCS. If the device send a correct response that means the RS485 chip on the MDS100-BW is good.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

raan

  • Newbie
  • Posts: 31
    • View Profile
Re:Dead RS485 Nano Display
« Reply #2 on: March 04, 2011, 07:02:41 AM »
I decided since it is critical that I will just order another one.