« on: March 19, 2003, 04:28:20 AM »
Is it possible to branch outputs and include contacts in each branch (to avoid having to create multiple circuits that are only different by one or two contacts),I have attempted to do this within the ladder editor with no success,with contacts I can branch fine just not ouputs with contacts (parallel outputs work ok too)
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3179
    • View Profile
    • Internet Programmable PLCs
Re: Branching outputs
« Reply #1 on: March 19, 2003, 05:07:45 AM »
What you are trying to do is to have branches from the within a circuit. This is implemented using the [ILock] and [ILoff] functions. See TRiLOGI manual for details on these two functions, or click on the following link and scroll down to find the [ILock] function:

http://www.tri-plc.com/TLeval/Help/specialfn.htm