Hi
the pwm pin output#7 max output current 10A
does it  mean source 10A to the load? how long can it last?
output voltage when on: 1V@10A NOT 12V@10A???
THANKS

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3179
    • View Profile
    • Internet Programmable PLCs
Re:pwm chanel 1 10A
« Reply #1 on: March 09, 2009, 11:33:38 AM »
On T100MD888+ the peak output current it can sink is 10A. When OFF, the output has a weak pull up to the PLC's positive terminal but when it turns on it goes to 0V and can sink peak 10A but continuous 2A only.

On T100MD2424+ the peak output current it can SOURCE is 10A and continous current is 2A. The output = 24V when turns ON and floating when it is OFF.

On T100MD1616+ the output sinks 1A max and 250mA continuous.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

kenobe

  • Jr. Member
  • Posts: 66
  • I'm a llama!
    • View Profile
Re:pwm chanel 1 10A
« Reply #2 on: March 10, 2009, 02:15:04 AM »
Hi
Thanks but
for tm100md888 , how long (time ) can the peak current last? 10ms?

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3179
    • View Profile
    • Internet Programmable PLCs
Re:pwm chanel 1 10A
« Reply #3 on: March 10, 2009, 05:35:39 AM »
It should be able to sink 10A for at least 1 second. The problem is not the driver's capacity, but the heat generated need to be dissipated via heat sink (not attached to driver) if it conducts 10A for prolonged period.
Email: support@triplc.com