Hi Support,
I have already performed this test, please refer to my post on 19 Jan 05:17:
"I have done a further test where I completely disconnected the PLC from everything and applied 3.88V (3 x AA cells) to output 4 and 0V. The measured current was 4.5mA and I noticed that the LED next to the power supply connector was faintly glowing."
I know that there is at least one other component in my system that is contributing to the issue and I am dealing with that seperately.
I disagree with your first comment, as it would be expected that an output would be off (open cct) when a unit is depowered otherwise there is no failsafe capability. If the PLC and all loads are on the same cct failsafe is automatic but I am sure there would be many applications using seperate supplies especially with remote IO apps.
Perhaps you could perform the test I have conducted on a PLC you have there. It may be that the batch I have has a faulty component.