Author Topic: E10  (Read 7567 times)

EDGAR

  • Jr. Member
  • Posts: 60
  • Automating concepts around the world!
    • View Profile
    • Kinemics
E10
« on: September 28, 2007, 08:06:18 AM »
Does the E10 support Special Bits like the other please? if so how can i add one.

also, I'm designing a surge protector for industrial air compressors, i have the plc connected to the unit CT to 24V. i like to add a suppressor to the supply voltage, can you guys recommend a type of suppressor i can use.

Thanks,

Regards,
Ed Santiago
Low cost Modbus OPC DA Server, supporting Modbus RTU, ASCII, and TCP. Download your demo today! Go to www.kinemics.com/modbus.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3170
    • View Profile
    • Internet Programmable PLCs
Re:E10
« Reply #1 on: September 28, 2007, 01:44:46 PM »
E10 support a few special bits although less than those found on the H-series and M-series. When you insert a contact you can scroll using left/right cursor key and click on the drop down menu to select special bits table.

I am not sure how your surge protector work but do take note that E10 does not have analog i/os. For surge suppressor consider one of those Transorb that can work rapidly to absorb voltage surges on the AC lines.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

EDGAR

  • Jr. Member
  • Posts: 60
  • Automating concepts around the world!
    • View Profile
    • Kinemics
Re:E10
« Reply #2 on: September 30, 2007, 03:07:36 PM »
I'm just detecting a Transfer switch from Normal power to Emergency power. that occure in 10 ms so the units stays with no power for 10 ms.
I programmed the E10 and it detect the voltage drop faster than my eye can blink it worked. i just need it to add the suppressor to protect the plc.
 
in my version of winTRiLogic 3.5 for the E10 i don't get that table with the Special Bits. i can see it but can't select it.

Thanks.
Low cost Modbus OPC DA Server, supporting Modbus RTU, ASCII, and TCP. Download your demo today! Go to www.kinemics.com/modbus.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3170
    • View Profile
    • Internet Programmable PLCs
Re:E10
« Reply #3 on: September 30, 2007, 10:05:19 PM »
You should be able to select the special bit (sequencer or clock pulses) when you are creating a contact.  For E10 only a few of the special bits are available. The rest are shown as "-"


« Last Edit: September 30, 2007, 10:09:11 PM by support »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

EDGAR

  • Jr. Member
  • Posts: 60
  • Automating concepts around the world!
    • View Profile
    • Kinemics
Re:E10
« Reply #4 on: October 01, 2007, 10:36:43 AM »
Sure, I see the Special Bits on the Drop down box but is not allowing me to select it. I click on it but it goes back to the previously selected item.

Thanks.


Low cost Modbus OPC DA Server, supporting Modbus RTU, ASCII, and TCP. Download your demo today! Go to www.kinemics.com/modbus.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3170
    • View Profile
    • Internet Programmable PLCs
Re:E10
« Reply #5 on: October 01, 2007, 11:11:49 AM »
The picture I show to you above is when I try to insert a series contact and I picked up the Clk:1.0s special bit from the menu and it was inserted into the ladder circuit.

What were you trying to connect? Did you try to connect it as a coil? The special bit here can only be used as a contact on the ladder diagram and not used as a coil.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

EDGAR

  • Jr. Member
  • Posts: 60
  • Automating concepts around the world!
    • View Profile
    • Kinemics
Re:E10
« Reply #6 on: October 02, 2007, 02:52:16 AM »
I also use the WinTRiLOGIC for the TM888+ too.  I'm doing the same thing as you're showing me. But it doesn't work even if i click on the side arrows it doesn?t go over counters.
I will re-install the program again.
Thanks.
Low cost Modbus OPC DA Server, supporting Modbus RTU, ASCII, and TCP. Download your demo today! Go to www.kinemics.com/modbus.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3170
    • View Profile
    • Internet Programmable PLCs
Re:E10
« Reply #7 on: October 02, 2007, 04:11:42 PM »
What version of O/S are you running? What version of JRE is being used? Hopefully a re-installation will work.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS