Author Topic: T100MD888+ Power supply  (Read 12192 times)

ondulado

  • Newbie
  • Posts: 0
  • I love YaBB 1G - SP1!
    • View Profile
T100MD888+ Power supply
« on: November 12, 2003, 02:47:10 AM »
What is the minimum voltage to fed the PLC in "12V mode" ?
We have a 100V - 140 VDC source (batteries). How can we feed the PLC ?
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: T100MD888+ Power supply
« Reply #1 on: November 14, 2003, 07:47:05 AM »
When using in 12V configuration, the power supply should be regulated at 12V DC and should not dip below 10.5V at any time.

Your high voltage DC source should be stepped down using a DC-DC converter to 24V DC before connecting to the PLC. At such high voltage there isn't other safe or cheap method of connection.  Check with Vicor for a suitable product:  http://www.vicr.com
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS