Author Topic: Serial communication in Labview/Hyperterminal  (Read 14790 times)

Esho Kasey

  • Guest
Serial communication in Labview/Hyperterminal
« on: June 10, 2002, 11:43:50 AM »
Hi all,

I wanted to communicate serially with the PLC using LabVIEW but was unable to do so. I also tried sending commands in Hyperterminal but the PLC did not respond (i.e. i typed IR* and nothing followed...) but when i do it in TLserver it works. Can anyone help me out seeing that i am fairly new to PLCs. Thank you.
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: Serial communication in Labview/Hyperterminal
« Reply #1 on: June 11, 2002, 06:51:03 AM »
To use HyperTerminal to talk to the PLC, you have to enter the multi-point version of the command:

@01IR00*

and you should get a response. The point to point version require the HyperTerminal to send a "Ctrl-E" character before sending the string "IR*".

« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS