Author Topic: FMD88-10 with FRAM-RTC256 switch 1  (Read 11250 times)

Philippe Parmentier

  • Newbie
  • Posts: 29
  • new in plc
    • View Profile
FMD88-10 with FRAM-RTC256 switch 1
« on: January 16, 2014, 03:29:23 PM »
Good day all,

I've noticed a ladder execution time slower when the Switch-1 is ON (so the memory variables become non-volatiles)

For testing I'm incrementing X at every ladder scan and every seconds, I'm displaying the sum and resetting to 0

Switch-1 OFF : Volatil memory : 975 ladder loops/sec
Switch-1 ON  : Non-Volatil memory : 820 ladder loops/sec

Is it a normal behaviour?

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:FMD88-10 with FRAM-RTC256 switch 1
« Reply #1 on: January 17, 2014, 11:59:52 AM »
With DIP switch #1 ON, every write to the A to Z and DM 1 to 1000 a copy will be written also to the FRAM, which takes more time to execute than without DIP switch #1 being turned ON.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS