Author Topic: ReadMB2 Number of Registers  (Read 12169 times)

eagroup

  • Newbie
  • *
  • Posts: 4
  • I'm a llama!
    • View Profile
ReadMB2 Number of Registers
« on: September 03, 2010, 10:47:21 AM »
The M-series READMB2 command is limited to reading 16 registers.  Has this been increased for the Nano or F-series?  I need to read 250 registers from 4 devices and I'd rather read them, for instance, 100 at a time.

Thank You.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:ReadMB2 Number of Registers
« Reply #1 on: September 06, 2010, 03:09:55 PM »
The current limit of READMB2 command for Nano-10 and F-series PLCs 32 words per read command.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

eagroup

  • Newbie
  • *
  • Posts: 4
  • I'm a llama!
    • View Profile
Re:ReadMB2 Number of Registers
« Reply #2 on: September 07, 2010, 09:20:25 AM »
Similarly, when the M- or F-series is acting as a slave, how many registers can be requested at a time by the master over RTU or over TCP?

Thank You

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:ReadMB2 Number of Registers
« Reply #3 on: September 07, 2010, 04:32:13 PM »
As a Modbus RTU or Modbus TCP slave you can access 122 data point max.

As a Modbus ASCII slave you can access only half the number (61).
Email: support@triplc.com
Tel: 1-877-TRI-PLCS