Internet PLC Forum
Welcome,
Guest
. Please
login
or
register
.
1 Hour
1 Day
1 Week
1 Month
Forever
Login with username, password and session length
News:
Home
Help
Search
Login
Register
Internet PLC Forum
»
General
»
Technical support
»
ReadMB2 Number of Registers
« previous
next »
Print
Pages: [
1
]
Author
Topic: ReadMB2 Number of Registers (Read 12169 times)
eagroup
Newbie
Posts: 4
I'm a llama!
ReadMB2 Number of Registers
«
on:
September 03, 2010, 10:47:21 AM »
The M-series READMB2 command is limited to reading 16 registers. Has this been increased for the Nano or F-series? I need to read 250 registers from 4 devices and I'd rather read them, for instance, 100 at a time.
Thank You.
Logged
support
Global Moderator
Hero Member
Posts: 3174
Re:ReadMB2 Number of Registers
«
Reply #1 on:
September 06, 2010, 03:09:55 PM »
The current limit of READMB2 command for Nano-10 and F-series PLCs 32 words per read command.
Logged
Email: support@triplc.com
Tel: 1-877-TRI-PLCS
eagroup
Newbie
Posts: 4
I'm a llama!
Re:ReadMB2 Number of Registers
«
Reply #2 on:
September 07, 2010, 09:20:25 AM »
Similarly, when the M- or F-series is acting as a slave, how many registers can be requested at a time by the master over RTU or over TCP?
Thank You
Logged
support
Global Moderator
Hero Member
Posts: 3174
Re:ReadMB2 Number of Registers
«
Reply #3 on:
September 07, 2010, 04:32:13 PM »
As a Modbus RTU or Modbus TCP slave you can access 122 data point max.
As a Modbus ASCII slave you can access only half the number (61).
Logged
Email: support@triplc.com
Tel: 1-877-TRI-PLCS
Print
Pages: [
1
]
« previous
next »
Internet PLC Forum
»
General
»
Technical support
»
ReadMB2 Number of Registers