F 2424 and MD-HMI
« on: March 25, 2010, 09:28:06 AM »
I am using this F2424 for the first time. The display is working fine but I am not seeing the keypad inputs when pressed using online monitoring. I am using the same key routine from your samples that I have used with the T100MD2424+.

I see no mention to the base address for the F2424 when using the MD-HMI Am I correct that it is the same as the T100MD2424+ ?

The zero key starts at input 25 and input 40 is the last input for the F4 key.

My program works fine in simulation, just not with the hardware.

Possibly I have a hardware problem with the keypad that does not effect the LCD?

Thanks

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:F 2424 and MD-HMI
« Reply #1 on: March 25, 2010, 10:34:22 AM »
Did you plug in the 10 way connector into the Expansion socket (on the right edge of the PLC). It is a common tendency for F-series user to plug into the socket next to the LCD display. I know it may sound logical but that socket next to the LCD socket is reserved for future implementation of CANbus and is not currently used.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

cch1955

  • Full Member
  • Posts: 198
  • Automated Machine Systems Designer
    • View Profile
Re:F 2424 and MD-HMI
« Reply #2 on: March 25, 2010, 11:51:19 AM »
A simple solution. Another guy plugged in the cables and I did not notice the location.

I moved the cable and all works well.

Thanks for the prompt reply.