Author Topic: LM335 IC sensor  (Read 13597 times)

Fernandz

  • Newbie
  • Posts: 10
    • View Profile
LM335 IC sensor
« on: October 30, 2003, 02:41:03 PM »
What would be the best way to hook up a LM335 sensor to the analog inputs of the T100MD? Also what formula would i have to use?
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: LM335 IC sensor
« Reply #1 on: October 31, 2003, 10:08:40 AM »
Since the LM335 has output of 10mV/K, you can wire up the sensor such that its output voltage fall within the range of the PLC's analog inputs (0-5V for most PLC or 0-1V for 2 of T100MD1616+)  and then you will be able to measure the voltage. The reading obtain is 0-4092 which can be scaled to units you want.

For other interface circuits for LM335, check with NS data sheet:

http://www.national.com/ds.cgi/LM/LM135.pdf
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS