Author Topic: 1616 Relay expansion  (Read 10321 times)

IANRAL

  • Newbie
  • Posts: 2
    • View Profile
1616 Relay expansion
« on: March 13, 2005, 05:39:50 AM »
Am new to this.

Have a T100MD-888+ connected to a EXP1616R. Am writing a proram for this and wondered where the 16 relay outputs will show up--that is what output number I should assign to them in the program, the manual mentions the input numbers to use for the expanded inputs but not the relay outputs.

Thank you

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:1616 Relay expansion
« Reply #1 on: March 13, 2005, 11:30:48 AM »
A single EXP1616R connected to T100MD888+ will start from output #17 to #32 as well as input #17 to #32. Input #9-16 and output #9-16 are not used on T100MD888+.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS