Author Topic: question on D.O.  (Read 17245 times)

edgar

  • Guest
question on D.O.
« on: December 04, 2004, 09:21:59 AM »
hey i bought the t100md+ and i have a question regarding D.O.
when the led is on the Output is off and when the led is off the output is on is that corect...?

i check with my m.mitter and the above is what i got
Led on = off
Led off = On
that's the way it is....

WireNut

  • Guest
Re:question on D.O.
« Reply #1 on: January 29, 2005, 03:24:33 PM »
The reason that it appears the outputs are ON as you said when the LED is off is because they are DC Sink outputs.  That is, when they are logical 1 (ON) they SINK to ground.  If you are testing output voltage to ground then you will see inverted logic (Outputs are internally pulled up to +V).  In order for the outputs to respond in true logic, the + terminal of the powersupply should be connected to the + of the load and the ground or negative terminal of the load should be then connected to the output terminal.  The output will be +V (24 or 12V) when off and 0 volts (approx.) when on.

By applying 0 volts (ground terminal) to the negative of the load (relay, solenoid, motor etc.) is just like putting a switch in the negative wire rather than the more conventional positive wire.

I hope this helps.

WireNut