Author Topic: Modbus addresses  (Read 12561 times)

dushyantbangal

  • Newbie
  • *
  • Posts: 3
  • I'm a llama!
    • View Profile
Modbus addresses
« on: September 11, 2017, 05:06:34 AM »
I want to read some data by querying my Nano10 PLC using ModbusTCP.

I was able to get DM[1] value at address 782. But I was not able to get DM[2] at 783.
However, if I put 782 and read range of registers, I get the next DM values.

Is there a list of different registers and their modbus addresses?

garysdickinson

  • Hero Member
  • Posts: 502
  • Old PLC Coder
    • View Profile
Re:Modbus addresses
« Reply #1 on: September 11, 2017, 11:19:51 AM »
The first problem is that the correct Modbus register address to access DM[782] should be 1782 not 782.  The basic rule to generate a Modbus register address for DM[n] addressing is to add 1000 to "n".

If the Nano-10 responds to Modbus address 782, it is not documented as to what address 782 might contain.  I cannot explain what you are seeing if you attempt to read multiple registers from the Nano-10 starting at modbus address 782.

The internal Modbus addresses are documented (hinted at) in the Nano-10 User Manual version 7.2 in figure 14.6.1.1

I have a couple of suggestions:

  • Write a PC6 program that contains a single custom function that runs on the first scan of the ladder logic. This CF should write an incrementing 16-bit pattern to each of the DM[] locations.   This is what I'd suggest:
Code: [Select]
' Fill Nano-10 DM[n] locations with a value equal to the index, "n", for each of the
'   1000 DM[] registers supported by the Nano-10
'
for i = 1 to 1000
   DM[i] = i
next
Now you know exactly what to expect when accessing any DM[] location.
  • Change your Modbus TCP/IP program to use the correct registers address for DM[n].  Now see if you are actually getting the correct data from the Nano-10
  • Use a Modbus test program that allows you to see exactly how the Nano-10 responds.  I have used Chipkin Automation Systems CAS Modbus Scanner for both Modbus TCP/IP and Modbus RTU with the PLCs as clients and many other Modbus devices.  This is a free program at:

http://www.chipkin.com/products/software/modbus-software/cas-modbus-scanner/
[/list]

Best of luck,

Gary D*ckinson