Author Topic: high speed counter  (Read 12295 times)

jbrandall

  • Newbie
  • Posts: 19
  • farmer boy
    • View Profile
high speed counter
« on: July 16, 2013, 02:58:11 PM »
why does my high speed counter start to count down when input(3) pulse stop coming?  all else it seems to work ok.  I do use PMON 2 to monitor input(4).  When that stops, the counter stops counting down.  What do I do??

jbrandall

  • Newbie
  • Posts: 19
  • farmer boy
    • View Profile
Re:high speed counter
« Reply #1 on: July 17, 2013, 07:57:19 AM »
follow up.  if I do PMOFF 2 the counter seems to work right.  the problem is that I need to monitor imput 4 for speed (rpm) and want to use input 3 for the high speed counter because of the interrupt feature.  is there any way to uncouple the linkage between input 3 and input 4?  I have no spare inputs to juggle so as to leave half a pair disconnected.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:high speed counter
« Reply #2 on: July 19, 2013, 01:14:04 PM »
High speed counter are designed mainly for quadrature counter and hence uses both inputs #3 and #4.

Are you using single phase counting? When input #3 is used as single phase HSC input #4 controls the direction of count (increment or decrement).

As such these two inputs cannot be uncoupled since they together serves the HSC.

If the speed is not too fast you could implement input #3 as an interrupt input and increment/decrement a variable (e.g. C =  C+1) whenever the interrupt service function is run.

This way input #4 can still be used as PMON input and it may do what you want.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS