Author Topic: Strain gauge  (Read 11598 times)

can

  • Full Member
  • Posts: 160
  • I'm a llama!
    • View Profile
Strain gauge
« on: February 18, 2010, 08:04:46 AM »
Hi. How can I get readings from strain gauge? Can MD888 do it?

Thanks

Regards
Ken

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Strain gauge
« Reply #1 on: February 18, 2010, 11:23:32 AM »
If you configure your strain gauge into a wheatstone bridge and can output signal in the range of 0 to 5V then the PLC can read the signal using its analog inputs.  If the signal level is too low then you may need a signal conditioner to amplify the signal to 0-5V range so that the PLC can measure the voltage and provide a reading for the force.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

can

  • Full Member
  • Posts: 160
  • I'm a llama!
    • View Profile
Re:Strain gauge
« Reply #2 on: March 02, 2010, 06:40:04 PM »
I have a load cell that states 1mv/v that I want to connect to plc for fast response reading. The signal from the load cell will go through an amplifier that has a 12v input. There is FG, GND on the amplifier also. Anyone knows what it stands for? Can I use the MD888 for the purpose?

Thanks

Regards
Ken