Author Topic: Computer(s) won't see PLC any more - Please help  (Read 12309 times)

paigeh

  • Newbie
  • *
  • Posts: 1
  • I'm a llama!
    • View Profile
Computer(s) won't see PLC any more - Please help
« on: September 07, 2007, 03:48:10 PM »
Hi,

I hope someone can help! We have programmed the PLC, and have been communicating with the computer via a 9-pin RS232 cable. Things were working fine, and we updated the program successfully several times. Now, however, the computer will no longer recognize the PLC. We have tried using a different cable, and we even tried two other computers. We have a critical update that has to be done, and we can?t get to it.

Thanks for your help! You can?t imagine how happy we will be when we solve this!

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Computer(s) won't see PLC any more - Please help
« Reply #1 on: September 07, 2007, 05:38:39 PM »
What PLC model? If it is M-series is it because the PLC program has changed the comm port settings? Tried to turn ON DIP switch #4, reset the PLC and use TLServer (with baud rate set to 9600) to type in "IR*" at the serial port setup page and see if you get a response. If so, clear the PLC program with a blank program, turn OFF dip switch #4 and put TLServer baud rate back to 38,400bps and things will work normally again.