Author Topic: Analog Output on the TM100+ 4832  (Read 14302 times)

jrustang

  • Newbie
  • Posts: 16
  • The Shadow!
    • View Profile
Analog Output on the TM100+ 4832
« on: September 05, 2007, 08:45:35 AM »
Hi, I'm trying to use the analog output 7 and 8 of the PLC TM100+ 4832, but I'm having a problem. After i execut  the ?setDAC? command on the respective channel(s) I test with a Multimeter (the - on the AVss and the + to the Output channel that I want to use) to see how many volts are coming out, But I get nothing. Any Idea for this Newbie... Thanks

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Analog Output on the TM100+ 4832
« Reply #1 on: September 05, 2007, 09:23:56 AM »
T100MX-4832 requires a user-supplied 5V external analog reference voltage connected to its AVcc terminal. So please connect a 5V voltage source to its AVcc and AVss terminal and you will then be able to get 0-5V output on its two DAC channel based on the SETDAC value.

As the AVcc signal goes directly to the CPU please ensure that only the correct voltage is applied to this pin otherwise the CPU can be permanently damaged if a wrong voltage is applied.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

jrustang

  • Newbie
  • Posts: 16
  • The Shadow!
    • View Profile
Re:Analog Output on the TM100+ 4832
« Reply #2 on: September 05, 2007, 10:31:28 AM »
Thank you for your answer.
I already had conectet the 5v power supply and is well conectet 'because I have allready install an analog divice on the analog input number 1 and is working fine. And that's why I don't find an explanation why is not working

Have Another Idea that can help me?

Thank you very much !!!

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:Analog Output on the TM100+ 4832
« Reply #3 on: September 05, 2007, 09:30:14 PM »
Remember that AD#7 shares with DA#1. AD #7 pin shares with DA#2, so your command should be:

 SETDAC 1,2048
 SETDAC 2, 1024

Then measure on the analog DB15 connector at pin 2 and pin 1 respectively. Pin 8 is for Analog input 1, pin 7 for AI #2,....

« Last Edit: September 05, 2007, 09:31:14 PM by support »
Email: support@triplc.com
Tel: 1-877-TRI-PLCS

jrustang

  • Newbie
  • Posts: 16
  • The Shadow!
    • View Profile
Re:Analog Output on the TM100+ 4832
« Reply #4 on: September 06, 2007, 07:54:00 PM »
That's why you need to talk to the expert ones....
That was the answer...  Thank you...!!!