Author Topic: De-Bouncing  (Read 11919 times)

dan

  • Newbie
  • Posts: 47
    • View Profile
De-Bouncing
« on: June 14, 2007, 08:10:51 AM »
Hi,

What will be the best way to de-bouncing 9 inputs on the T100.
I would like to do this thru programing and if is possible to be able to adjust it.

Thank you,

Dan

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:De-Bouncing
« Reply #1 on: June 14, 2007, 10:46:49 AM »
You can connect each input to one timer with say a 0.2s time-out. The timer contact will be the one that is actually used to trigger a process. As long as the input is bouncing with cycle time of less than 0.2s, the timer will be reset repeatedly. Only when the bouncing stop then the timer has a chance to time out and the its contact become a debounced input to the program.

Email: support@triplc.com
Tel: 1-877-TRI-PLCS