Author Topic: T22H-NPN reset problem  (Read 10992 times)

Hans Karrais

  • Guest
T22H-NPN reset problem
« on: July 06, 2003, 01:17:30 PM »
I'm unable to reset my T22H-NPN.
After loading several test programs that worked great, on the last one the PLC froze up.  Outputs 1 through 4 are constantly on and can not be reset.  I'm able to communicate with the PLC and load new programs but I can't reset it.  Help would be very much appreciated.
Thanks
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: T22H-NPN reset problem
« Reply #1 on: July 06, 2003, 05:28:52 PM »
Does the PLC output appear as ON during online monitoring? If online monitoring shows that your output is off, yet the output LED turns ON, it means that the output driver has probably blown.

The output drivers on T22H-npn are controlled by the ULN2003A. You can try to swap the ULN2003A that controls output 1-4 with the other chips and see if the output problem has shifted. If so, it confirms that the output driver is fried.

The most likely reason for the output driver to blow is over current. Wrong polarity connection to the PLC's power supply input can also knock out the output driver.

You can purchase the ULN2003A driver chip easily from any Radioshack or any local electronics store,  or you can purchase it from us.  Please send your request to sales@tri-plc.com if you wish to purchase the ULN2003A chip.
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »