Technical support / Re: PLC INPUT Interrupt Behavior
« on: October 06, 2022, 09:42:05 PM »
I wrote some test code to see if I could figure out how long it takes from the time that an active INPUT ISR is turned off via the IntrOff statement to when the state of the physical INPUT can been "seen" by ladder logic.

The amount of time is 2 to 3 scans of the ladder logic. In most cases it takes 2 scans.

I have attached a image of the ladder logic and the complete program for the test to this reply.

The CF, Ch1FndLowSw sets up the interrupt for the INPUT[1] and issues a StepMove command.  The RELAY, GO, will invoke the CF.

The ISR CF, Ch1LmtSLo_Int, will be triggered when the INPUT[1], Ch1LmtSwLo goes active. The ISR is configured to respond to a rising edge event.  The ISR does two important things:
1. Turns off the ISR
2. Sets the RELAY, Ch1Intr to indicate that the interrupt has been serviced.

The CF, IncScanCount increments the TBASIC variable A on each scan of the ladder logic that the CH1Intr RELAY is active.

The PLC code is very simple.  Just complicated enough to answer some of my questions.

Best regards,

Gary Dickinson

17
Technical support / PLC INPUT Interrupt Behavior
« on: October 05, 2022, 03:12:18 PM »
I have been working on using the INPUT interrupts that are tied to end limit switches for a stepper based motion system.  I have gotten them to work, but am a little confused about the timing.

This is the code for one of the ISRs:


' Ch1LoLmtISR - Interrupt handler for Ch1LmtSwLo
'
' This code aborts the CH1_Y stepper system when the interrupt condition is met
'
StepStop CH1_Y          ' Abort Stepper Motion
IntrOff Ch1LmtSwLo_Int  ' Disable interrupts for this Input
SetIO Ch1Intr           ' Set ISR event RELAY


I am aware that while an ISR is active, following the execution of IntrDef, that the INPUT pin status is NOT latched at the end of the ladder logic scan. When the ISR for an input is disabled, the INPUT status is "visible" to ladder logic.  So my "initial fix" was to re-sych the Ch1Intr RELAY at the end of the ladder logic to control a 2nd RELAY, Ch1IntrDly, with something that looks like this:

Ch1Intr
----||-----------------------------------------(Ch1IntrDly)

My assumption is that if the ISR set CH1Intr then waiting one scan time the delayed version of CH1IntrDLY in ladder logic, that the physical INPUT would be visible to the ladder logic.

Sometimes this works and sometimes it does not.  So I added more logic to delay the CH1Intr by a 2nd scan and this worked a bit better, but sometimes failed.

Ch1IntrDly
----||-----------------------------------------(Ch1IntrDly2)

Ch1Intr
----||-----------------------------------------(Ch1IntrDly)

My "ultimate" fix was to make Ch1IntrDly a TIMER and not a RELAY. This will result in multiple scan times before the TIMER goes off.  Now everything is visible to the ladder logic.

Do you have any suggestions on a better approach to "know" when the INPUTs are working after turning off an INPUT interrupt?

Is there some other timing issue that I am missing?

Does the SetStop take a lot of time to execute? If so should I have rearranged the order of the lines of code in the ISR?
Does the IntrOFF statement take effect immediately, or is it delayed to some point in time that is tied to the ladder logic scanner?

Beat regards,

Gary Dickinson

18
Technical support / Re: Small quibble on Version 7.5 Build 14
« on: September 09, 2022, 10:16:21 AM »
I have another small quibble about the output from the Print Control Panel.

It has to do with the printing ladder logic that uses labels for contacts that are greater than 8 characters in length.  The issue is that the labels simply run together and are difficult to read.

I have attached a couple of screen shots, one showing what the i-TRiLOGI editor page looks like and the other the printout.

I couldn't find a way to decrease the size of the text used for the label or to increase the spacing between contacts in the ladder logic rung.

Is there something that I am missing?

Gary D

19
Technical support / Re: EZWire1616 Stepper controller OUTPUTs
« on: September 08, 2022, 02:26:10 PM »
Thanks the direct links to the documentation works on both my desktop PC and iPad.

The version of the website that is served to my iPad is the culprit. The links to some of the reference documents are broken.

One other documentation question. There is an on-line view of the TBASIC programming manual that can be reached from the I-TRiLOGI app.  Is there a version of this that I can download as a PDF.

Gary d

20
Technical support / Small quibble on Version 7.5 Build 14
« on: September 08, 2022, 02:12:25 PM »
The Print Dialog box gets overwritten with parts of the displayed .pc7 file after pressing on the "Print" button.

See attachment

Gary D

21
Technical support / Re: EZWire1616 Stepper controller OUTPUTs
« on: September 08, 2022, 01:04:45 PM »
Thanks for the quick feedback.  I was using "32" as the channel ID.  The code was originally written in 2015 and run on a Fx1616-BA.

The "32" ID is documented only in the Fx1616-BA User Manual.  This manual is not available for download from your website.  These inks return 404 errors:

https://triplc.com/documents/Fx1616-BA-UserManual.pdf
https://triplc.com/documents/Fx1616-BA_Product_Info_Sheet.pdf

Thanks,

Gary d


22
Technical support / EZWire1616 Stepper controller OUTPUTs
« on: September 07, 2022, 08:32:14 PM »
I am working with the EZWire1616 and have run into some questions with the stepper control mechanism.

I am using CH1 and CH2 to drive external stepper drivers using
PULSE and DIRECTION signals.

The user manual that I can find is Rev 1.0 dated 3/17/2016.  It shows support for 3 steppers with the control signals on OUTPUTS 5 and 6 for CH1. OUTPUTS 9 and 10 for CH2 and 13 and 14 for CH3

The issue is that the CH2 OUTPUTS appear to be actually using 7 and 8 and NOT 9 and 10.

Other documentation on the website says that this PLC only supports 2 steppers and not 3.

Questions:

What is the correct wiring for CH2?
Is there support for CH3 if I need it?
Is the more accurate documentation available for this PLC?

Gary Dickinson

23
Neal,

Good to hear that you have gotten stuff to work. 

I don’t know the answer to your question about connecting two Ethernet devices together with a single cable.  In the old days this required a cross over cable. However in modern times most Ethernet transceivers will work with cables that have the paired signals reversed.  Give it a try.

Another thing you can do is to put all of your devices on RS485.  The HMI will be the master and can access registers and coils in both the PLC and the temp controller.

As an example, I have a client that uses an FMD (integer PLC) with a Weintek HMI. The PLC needed to solve a complex bit of math that was best done in floating point.

The solution was to use DM32[] to hold the data to be processed and to hold the results. 2 PLC RELAYS were used. One to request that the HMI PROCESS the integer data. The second RELAY was set by the HMI after the data was processed and the results had been written back into DM32[].

In your application you could have the HMI poll your Temp controller periodically and update PLC registers with this data.  You could have the HMI program the temperature controller on request of the PLC.  Same approach, PLC data and one or two RELAYs for handshake.

If this craziness is of interest, l can post how to write a periodic HMI macro.

Gary d






24
Technical support / Re: NANO-10 and Weintek MT8050iE 4.3" Touch panel
« on: August 11, 2022, 09:45:56 AM »
Neal,

You have 3 devices connected to RS485.  Not a problem.

38400 BAUD is not a problem. I use this rate between the HMI and the PLC for all my projects. 

The HMI will act as a master device to talk to the PLC and the TX4S.  The PLC cannot talk directly to the TX4S. If the PLC attempts to talk to the TX4S then you have two master devices on the RS485 cabling and this will result in garbled communication.

Disconnect the TX4S and kill off any code in the PLC that talks with the  TX4S .  Now get the HMI/PLC working.  I worry about the HMI serial interface may be galvanically isolated.  If it is you will need to run a wire between the PLC 0V power input to the HMI'S signal ground pin for the RS232 port to them on a common ground reference.

Make certain that the PLC and TX4S are configured to respond to different Modbus IDs.

If your only choice is to connect all 3 devices on a single RS485 bus, then you can have the HMI query the TX4S, periodically and them update variables in the PLC.  This can be done with the use of a macro in the HMI.

I do not use the HMI drivers that are available for the TRI PLCs.  These drivers are NOT supported by Weintek and they don’t consistently support to all of the PLC's 32 bit variables. The Weintek Modbus drivers work fine and can be configured to get the word order correct for all of the 32 bit variables for all of the TRI PLCs.

Gary d
.


25
Technical support / Re: Nano10 RS-485 Modbus termination
« on: February 26, 2022, 03:04:22 PM »
Very good work at sorting the RS-485 communications.  This is a very old communication scheme and you have done some old-school trouble shooting.

The issue with the need to bias the RS-485 lines makes perfect sense. I have been lucky in that the external devices that I have worked with all used modern RS-485 Transceivers that didn’t require the biasing circuitry.

Gary d

26
Technical support / Re: Nano10 RS-485 Modbus termination
« on: February 22, 2022, 03:09:19 PM »
I have connected many Modbus devices to Nano-10s. 

If you are working with 6' of cabling at 9600 BAUD there is no need for termination resistors. Trust me on this.

I wouldn’t mess with the cable pull up/down resistors either.  The RS485 transceivers on the nano-10 are designed to bias the RS-485 bus so that the signal wires will not drift, when no device is transmitting, to a voltage that would be mistaken for the start of a character.  This is probably not your problem, either.

OK. What should you try?  I’ll give you a hint.  RS-485 is NOT a 2 wire interface.  All of the RS-485 transceivers must be referenced to a common signal ground to operate reliably.

I have worked with several devices that use an electrically isolated RS-485 interface. Many of these devices are 3 phase motor controllers sometimes called "inverters".  The RS-485 port on these devices are electrically isolated from both the high voltages as well as the 24V DC logic supply.

If your device(s) have isolated RS-485 ports, then you MUST connect the signal ground of your isolated port(s) to the “-“ power supply input of the Nano-10.  This is the third wire for RS-485.

If you are using a USB/RS-485 dongle there is a good chance that the RS-485 port will behave as if it is isolated.  I always connect the signal ground on the dongle to the Nano-10 power supply "-“. If your dongle does not have a signal ground connection then you should buy one that has this connection.

Regards,

Gary Dickinson

27
Technical support / Re: Monitoring of Com 1 and Com 3 for Ascii
« on: November 18, 2021, 12:42:35 PM »
can,

I don't have an answer to why long messages are not accepted by the target device.

I assume that the target device is not a PLC.  So you don't have much visibility into what the device is "seeing" on it's end of the serial cable.

Since all of your print statements are are all on the same line of TBASIC and the total number of characters is less than the PLC transmit buffer size of 256 then my usual idea about gaps in the data stream probably do not apply.

OK so now I am down to other reasons that things might go south...

BAUD rate might be a problem.  If the target devices firmware is dumb, has a very short buffer or is just badly implemented firmware, then you may be sending characters faster that the target device can handle.  Drop the BAUD rate to something like 300 (about 30 characters per second).  If this fixes the problem then you have learned something about the target device. 

I run 9600 for my Modbus communications because it is fast enough for my applications. It is slow enough to not need termination resistors even with long cables.

If I  suspect the PLC programming is messing up the transmitted string, then i monitor the serial line to see exactly what is being transmitted.

COMM3 is RS485, you will need  a RS485 to USB dongle for your PC.  I use a shareware program named "Tera Term" to monitor the serial port that the USB dongle has been assigned by your PC.  This will allow you to both observe and log the data that is being transmitted from the PLC's COMM 3 port.

If you have one of the "smart" sampling oscilloscope most can decode ASCII serial data.

Good luck,

Gary D


28
Technical support / Re: Monitoring of Com 1 and Com 3 for Ascii
« on: November 13, 2021, 09:19:53 AM »
can,

On the receiving end, I would suggest that you not bother with the INPUT$(ch) function. The documentation leaves out a bit of its behavior:


To return a string obtained from communication port # ch.
ch must be a numeric constant between 1 and 8. The actual target hardware determines the valid port #. This function returns an empty string if there is no valid string waiting at serial port in order not to hold up the CPU.



These are some of the things not documented:

The maximum number of characters returned is limited by the string variable.  Most of TRI's PLC’s strings are limited to 70 characters.  EEP$ strings are usually 40 characters max.  If the message is 80 characters in length, you will have to make multiple calls to read the message.

The actual function does not return the end of line character.  So if your protocol uses an end of line character you will not see it.  If your protocol uses a pair of characters to mark end of line, CR and LF, it will discard one of the pair of characters and the other will be returned in the string.  I don’t remember what the function considers end of line.

If you receive a 0 length message, then the receive buffer is empty.  This does not always indicate that you have reached the end of message. If you wait a few milliseconds you may find that more characters have arrived.

Because of the string variable length issue, the loss of the end of line character and the detection that the receive buffer is empty, I find that INPUT$() is not worth the effort.

I use the function INCOMM(ch)  as it has fewer limitations. And, since you see all characters it is easy to detect the end of message.  It is an easier function to determine if the receive buffer is empty as it returns the value -1 on this condition.

Gary d

29
Technical support / Re: Monitoring of Com 1 and Com 3 for Ascii
« on: November 12, 2021, 11:42:13 AM »
can,

If your application is just to act as a simple store and forward device and does not interpret or validate the received messages, then you just need to check the state of the receive buffer on each scan of the ladder logic and copy any and all received data bytes to the transmit port.

I am assuming that your issue is non-trivial.

The simple answer about communication protocols that require > 256 characters to be transmitted or received is "maybe".

    Let's talk about sending long messages:
    • There is a 256 byte output buffer for each communication port. Characters are placed in the buffer as the result of OUTCOMM and PRINT statements. Characters are removed from this buffer by low-level PLC firmware.  This firmware moves the data into a second buffer of 16 to 32 characters that are managed by the the UART. The UART is responsible for converting the data into a series of bits and shipping them out as a serial data stream.
    • If you your outbound message is greater than 256 characters you will have to divide the message into chunks less than 256 to fit into the output buffer.
    • There is no mechanism in TBASIC to determine the state of the output buffer.  The only way to prevent corruption of the buffer is to pace the OUPUTCOM or PRINT statements.  If you communicating at 9600 BAUD each character takes 1.042 ms to transmit. If each of your PRINT statements sends 256 characters you will have to wait at least 267 ms between PRINT statements to prevent corruption of the output buffer.  You are hoping that the output buffer is empty before the next PRINT statement.

      Let's talk about receiving long messages:
      • There is a 256 byte receive buffer for each communication port. Received characters are placed into the 256 byte buffer by means of low-level PLC firmware.
      • The INCOMM(ch) command returns a value of -1 if the receive buffer is empty. I would suggest reading received data with this command and buffer it in DM[].
      • It is the responsibility of your TBASIC code to pull characters out of the receive buffer faster than they are received.  Failure to do so will result in corruption of the input buffer. If you are at 9600 BAUD then you must be able to receive 256 characters in 267 ms.
      • I would suggest checking for received characters on each scan of the ladder logic and reading all characters from the receive buffer if any are detected. Remember that at 9600 BAUD that characters will arrive every 0.001 seconds. You will have to buffer the received characters using DM[] or EPP (if you have installed the RTC 256K module).

        Let's talk about your communication protocol:
        • How tolerant is it with gaps in the messages that you will be transmitting?
        • If you are sending messages in chunks, then there will be gaps in time when no characters are transmitted. If you protocol has some sort of timeout mechanism, you will have to ensure that the transmit gaps are short enough so that the receiving end does not timeout and long enough that to prevent corruption of the PLC output buffer.
        • Modbus RTU expects a message to be sent without gaps between characters.  A gap is interpreted as an end of message. In order to not have a gap in output Modbus RTU frames, I buffer everything, compute the CRC and send the entire frame in one tight loop.  I limit the message size to less than 256 characters to avoid any gaps in the transmission.


        Gary D[/list][/list][/list]

        30
        Technical support / Re: Monitoring of Com 1 and Com 3 for Ascii
        « on: October 28, 2021, 02:14:39 PM »
        can,

        In regards to the meaning of the C programming construct of "\n" or newline, this is an operating system dependent behavior.  In UNIX \n translated to a linefeed.  In other operating systems it translated to a carriage return.  In CPM it was 2 characters a carriage return and a linefeed. So I have no clue what your device expects as a line termination sequence.

        I think your example would output "PASS<CR><SUB>".  The 26 value used by the outcomm statement got you the  < SUB > character.  I haven’t seen a communication protocol use this character.

        The Print #n statement prints 0 or more arguments separated by a semicolons, ";". if there is an ";" at the end of the statement, then print #n will not append an end of line character to the output characters.

        If there is no  ";" at the end of the statement, then the print #n statement will append an ASCII carriage return, CR or 0x0d, to the output.

        Samples:

        print #1 "hello";                      ---> sends "hello" only
        print #1 "hello"                       ---> sends "hello" and an ASCII CR
        Print #1                                 ---> sends ASCII CR only
        Print #1 "hello";"\0a";            ---> sends "hello" and an ASCII LF (linefeed) with a hex value of 0x0a
        print #1 "hello";"\0d\0a";       ---> sends "hello and an ASCII CR followed by an ASCII LF

        So you  are not to limited in controlling the end of line character(s).

        If you have to send an ASCII NUL or 0x00 then you need to use OUTCOMM.

        Gary D