« on: March 17, 2010, 10:09:01 AM »Did you run the SETPROTOCOL command in the PLC? Or did you change the PLC's baud rate settings using SETBAUD command? Both the HMI and the PLC must be set to the same baud rate, data bit, stop bit and parity configuration.Yes SETPROTOCOL is used but it is set to 0 (auto sensing) and SETBAUD = 6 (38400). The HMI is transmitting MODBUS ASCII, @ 38400 BAUD.
If you run the SETPROTOCOL make sure that it is set to the same protocol as your HMI. Modbus ASCII and Modbus RTU are very different and if you set it to one type of protocol it will not be able communicate properly.I am able to use Lamp displays and watch relays and outputs fire, but can not get anything from timers, counter, or DMs.