Technical support / Re: PLC comm problem/ PLC Inoperative
« on: December 01, 2003, 07:58:29 PM »
If the PLC seems to be working properly and you are able to perform online monitoring, yet unable to transfer new program to the PLC, then you type in the following command at the serial command prompt in the TLServer:
 
@01$cKILL00*
 
(notice small letter "c" and capital "KILL")
 
That would delete the corrupted program and password which must have been there because of the corruption.  You will need to re-transfer your program to the PLC because the original program in your PLC will be deleted.

3122
Technical support / Re: PLC comm problem/ PLC Inoperative
« on: November 30, 2003, 12:00:16 AM »
Will, I am a little confused. You mentioned that you tried the reset instruction described in this post to no avail. Yet you mentioned that when you went to the site later you found that the PLC is running properly. Does it mean that initially you tried the instruction remotely? How were you able to turn ON DIP Switch and perform the reset if you were not at the site?

If your PLC gets back to running properly after a overnight shutdown without your manual intervention or transfering the program to the PLC, then it is likely that it RAM copies of the PLC CPU has been corrupted by the electrical noise in the system but the EEPROM copy is still intact. So after a power down and reset, the PLC runs the program properly again.

Protecting the supply to the PLC is important. Power to the microprocessor electronics is like life blood to human being. The PLC I/O circuit already filtered most of the noise coming from the  I/O but the power supply noise goes directly to CPU.  

Diesel/gas power generator are pretty noisy fellow. However, most power surge filter on the market are for AC circuit. You may want to try to search for a DC power filter to improve the reliability of your system.

3123
Technical support / Re: PLC comm problem/ PLC Inoperative
« on: November 28, 2003, 01:02:50 AM »
Your program seems to have been corrupted and that may be the reason why it doesn't work. Please follow instruction in your installation guide on the use of DIP switch #4 to reset the PLC program. The following are the steps:

1) Turn ON DIP switch #4.
2) Reset PLC by turning OFF power and then ON again
3) Open "Serial Communcation Setup" in TLServer and change the baud rate to 9600. Then type in the command "IR*". You should get a "IR01*" in return.
4) Now, transfer a blank program into the PLC to clear out the corrupted EEPROM.
5) Turn OFF DIP Switch #4
6) Reset PLC as in 2)
7) Change the baud rate to 38400.
8) Now the PLC should be workable as per normal.



3124
Technical support / Re: Transfer protected by password
« on: December 02, 2003, 06:19:46 PM »
Can you try to transfer one of those simple sample program to the PLC and then power OFF and then ON the PLC again. Check if the PLC goes into PAUSE mode again. We want to be certain if it is due to your application program or there is some hardware problem in the EEPROM.

If the PLC pauses after reboot even with the simple demo program, then most likely the EEPROM chip may have suffered some damage during the power outage. You should email us at support@tri-plc.com providing us your full contact address and we can make arrangement for replacement of the PLC or the EEPROM chip.

3125
Technical support / Re: Transfer protected by password
« on: December 01, 2003, 10:01:01 AM »
Glad to learn that the issue has been resolved.

There is a watch dog timer to reset the PLC if the CPU goes hay-wire. In your case, the EEPROM corruption may not be due to a spurious write by the CPU, but an electrical transient via the power supply that may have directly erased the EEPROM.

You can use the "Change PLC ID" button in the TLServer to easily change the ID to any number from 00 to FF.


3126
Technical support / Re: Transfer protected by password
« on: December 01, 2003, 07:53:27 AM »
Indeed your EEPROM seems to have been corrupted. Can you type in the following command at the serial command prompt:

@01$cKILL00*

(notice small letter "c" and capital "KILL")

That would delete the corrupted program and password which must have been there because of the corruption.

3127
Technical support / Re: Transfer protected by password
« on: November 28, 2003, 12:53:52 AM »
Is this the first time you attempt to transfer program to the PLC using this computer? Have you previously successfully transferred a program to this PLC?

The "Transfer password" is a legacy feature in the DOS TRiLOGI software but is not enabled in TL5. So if you have never used the DOS TRiLOGI to enable the password then it is unlikely that you should receive a prompt for a transfer password unless your EEPROM has been corrupted or your COM port is not working properly.

Open the "Serial Communication Setup" in the TLServer and type in the following command:

IR*

What do you get in return? The correct response should be "IR01*"  (or other ID if you ever change that). If your response box returned "IR*" then you serial port is not a "real" serial port. What will happen is whatever you type will be echo back to you (try typing your own name). If this is the case, try to use another available COM port. Sometime Windows may report a COM port to TLServer that it cannot use for some reason. So change your com port selection to another working comm port number and re-try.


3128
Technical support / Re: crc+modbus
« on: December 04, 2003, 08:42:22 AM »
What PLC model are you using? Only the M-series PLC support the MODBUS protocol directly using the READMODBUS or WRITEMODBUS commands.  You can also implement other modbus functions using the TBASIC CRC16 function. Check the following threads for more details:

http://www.tri-plc.com/cgi-local/yabb/YaBB.pl?board=FAQ;action=display;num=1058204850


3129
Technical support / Re: NTC sensor
« on: December 05, 2003, 05:50:18 PM »
You mean Negative Temperature Coefficient? You need to built a circuit such that the resistance can be converted into voltage reading and connect that to the PLC's analog input. Then you can compute the actual temperature using either a formula or a lookup table.

3130
Technical support / Re: How to send an ASCII break from Com port?
« on: December 05, 2003, 06:04:00 PM »
Unfortunately the command set does not support the RS232 break signal that you mentioned. You will probably need to use a relay to switch out the RS232 transmit line and connect it to a +5V or higher when you want to send that 100ms "break" signal.

3131
Technical support / Re: How to send an ASCII break from Com port?
« on: December 04, 2003, 08:45:25 AM »
What is the ASCII code for the "ASCII Break" that you mentioned? You can use the OUTCOMM command to send any binary data from 0 to 255. However, it is assumed that the data are transmitted using the NRZ format of 1 start bit, 8 data bit, 1 stop bit and no parity.

3132
Technical support / Re: about your product cost
« on: December 08, 2003, 06:47:49 PM »
Yes, the T100MD888+ PLC with 8 digital inputs, 8 digital outputs, 6 analog inputs and 2 analog outputs are sold for US$199.00 each. However, first time user needs to get a "Starter Kit" for $259.00 that includes the T100MD888+ PLC, the Internet TRiLOGI programming software, the programming cable and all the manual.

3133
Technical support / Re: Certification
« on: December 08, 2003, 06:53:23 PM »
All our PLCs carry CE logo with declaration of Electromagnetic compatibility with the Euopean Union requirement.

However, all the PLCs do not require FCC or UL certification due to the low power nature of the product (UL Class 2 devices) and the way in which they are being used. You can however still use the PLC in equipment that are destined for UL listings.

3134
Technical support / Re: TRi-ExcelLink
« on: December 08, 2003, 07:11:53 PM »
The TRi ExcelLink writing interval is not meant to be very precise since it is based on a Java thread sleep time which can be affect by the execution of other application.

What you can do is to use the ExcelLink as a DDE server and then write a VB Script (Excel macro) that monitor the PC's internal clock and at the precise moment where you want to capture the data, you can activate the ExcelLink action that have been defined to capture the data into the spreadsheet. You can obtain more info about how to use the ExcelLink DDE server function from the ExcelLink help file or from the following link:

http://www.tri-plc.com/ExcelLink/ddecontrol.htm

There is a sample Excel spreadsheet file called "testmacro.xls" in your ExcelLink folder. You can open it and find out how to trigger the ExcelLink action from within Excel program.

3135
Technical support / Re: creating Menu System in ladder
« on: December 09, 2003, 08:24:58 AM »
I assume you are using the LCD display to create a menu structure. You will need to use a memory location (DM or A to Z) to keep track of where you are and then a custom function will display the correct text based on the pointer.

If you want to use 3 buttons to change set point, there is already an example in your "samples" folder called "SetTimerCtr_SV.PC5" which you can follow to learn to change any of the 3 timers or 3 counters in the PLC.