Internet PLC Forum

General => Technical support => Topic started by: PDirac on November 04, 2004, 05:37:36 AM

Title: Great PLC !!!
Post by: PDirac on November 04, 2004, 05:37:36 AM
Hi,

Your PLC with basic programming is great.
I measured a 0-8V Pirani sensor and I analysed the
data over a 15 hour period to find out I had a leak.
It saved me a lot of trouble  ;D
I am wondering if you guys plan to add floating point
arithmetic to your PLC or increase the resolution to
12 bit in a near future. ?
That would be great !

Best regards

Bob ;D
Title: Re:Great PLC !!!
Post by: support on November 05, 2004, 07:26:18 AM
Glad you enjoy programming the PLC.  Floating point and higher resolution ADC will be implemented in next higher power series of PLC but there is no scheduled date of release yet.

For T100MD+ PLC, you could use the I-7017 or I-7018 PLC to obtain 16-bit resolution ADC input. These two have isolated differential analog input that can very accurately measure analog quantities in fine resolution.