Hello,
I would like to communicate via the RS 232 between FMD88-10 and a masflow that communicates RS-232.
I try to send a string of such "070304716271620E" then Carriage Return and Line Feed.
I configured the same way the two products are: 1 start bit, 8 data bits, no parity and 1 stop bit.
My program:
in FirstScan
SETPROTOCOL 1.10
SETBAUD 1, & H06
then:
PRINT # 1 "070304716271620E" &H0D; &H0A;
FOR I = 1 to 10000
A $ = INPUT $ (1)
NEXT
By sending the same through the hyperterminal with my PC running Windows XP it worked! Can you help me this is quite urgent.
thank you
-
If your goal is to send a message terminated by a carriage return and a linefeed you might want to change the print statement from:
PRINT # 1 "070304716271620E" &H0D; &H0A;
to:
PRINT #1 "070304716271620E\0D\0A";
Your program, as presented, can not be compiled. It is missing a ";" . If your program was corrected so that it would compile:
PRINT #1 "070304716271620E"; &H0D; &H0A;
The output would be:
"070304716271620E 13 10"
There would be no carriage return and no line feed.
Best regards,
Gary D