Gentlemen,
Can you recommend a simple way of accepting an analog input of 0-10Vdc and converting the signal to a frequency output of 0-100Khz using the tri-plc? I will need to be able to trim the frequency as needed to achieve the desired output.
-
If you use a Nano-10, FMD or F-series PLCs you can set the PWM output frequency from 50Hz to 50KHz which is the maximum range that it can support.
For Nano-10, you can simply connect the 0-10V analog voltage via a 20K ohm series resistor to convert it into 0-5V analog voltage that the PLC can accept and a very simple program can be written to convert the analog input readings to PWM with varying frequency.
-
Thank you.
I see the PWM output is 24Vdc. My drive accepts differential, bipolar inputs at a level of 5V. Is there a recommended way to reduce the 24v to 5v?
-
Please refer to to Section 11.4.1 and 11.4.2 in the Nano-10 User's Manual that you can download from:
http://www.tri-plc.com/documents/Nano-10-UserManual.pdf
Two way of interfacing the 24V PWM outputs to 5V or 6V circuits are shown.
-
Thanks very much for the assistance!