General => Technical support => Topic started by: Samson on March 15, 2006, 05:13:47 PM
-
I was testing out the ADC on my T100MD1616+ using a 1k pot and external 5vdc. I grounded to the Analog 0v and used ADC #3. This is the Custom function im using.
setLCD 2,1,"Deviation :"+STR$(ADC(3))
Reguardless of what the voltage is at ADC #3 all I get on the display is 4092 and the same with the online monitoring. Is it a error in my programing or could it be a faulty chip on the board?
-Samson
-
Go to "Online monitoring", and click view, the ADC values are displayed, what happens when you ground the port or take it to the +5 volt Vref? You should see the extreme values of 0 and 4092. Are you sure the pot is OK?
-
I did monitor it with a DMM and could see the voltage going from 0vdc to 4.82vdc
I also tried this program for all ADC inputs (I have a 4x20 LCD)
1st Scan 1 FN_#1
---------||--------------------------------{dCusF}
Clk 0.5s 2 FN_#2
---------||--------------------------------{dCusF}
FN_#1
setLCD 1,1," Watch Dog 100"
setLCD 2,1,"Deviation :"
setLCD 3,1,"Amperage :"
setLCD 4,1,"Temperature:"
FN_#2
setLCD 1,15,CHR$(ADC(1))
setLCD 2,15,CHR$(ADC(2))
setLCD 3,15,CHR$(ADC(3))
setLCD 4,15,CHR$(ADC(4))
All I got on the screen is
4092
4092
4092
4092
I tried to ground all without result and tried the pot on all and nothing. It is very bizare. Is there a chip on the board that has just the ADC? Or is the ADC in the main CPU?
-Samson
-
I'm kind of a newbie also, but change the DCUSFUN to CUSFUN that will execute every scan. Not sure how the pulses go for that first scan only.
-
1st Scan scans the text to the screen only once. Then the ADC inputs are scanned every 1/2 second when the 0.5s closes.
-
Ok I reverse engineered the circuit board. I love doing that, I was having so much fun I got a nose bleed. Well I discovered that the #1 and #2 0-1v inputs go to a LM324N Quad Op-Amp.
http://www.alliedelec.com/Images/Products/Datasheets/BM/ON_SEMICONDUCTOR/On-Semiconductor_Actives-and-Passives_5684630.pdf
I set to 1k pot to 1v and traced it to pin 5 and pin 10. I read 1v on each but I read 0v on pins 7 and 8. Must be a bad op amp? Well I will get another tomorrow and hopefully that will work. Any insight on why this would be bad or possibly something I did? I always do an inspection to ensure everything is connected properly before turning the plc on after adding or changing the wiring. Although it has been 8 years since I worked with a plc and it was a 6502 programmed in assembly code. The I/O?s were UART 16550A with 16 byte FIFO, man what a dinosaur.
-Samson
-
Did you connect the analog power supply to the two terminals meant for that purpose? If you have connected the analog power supply correctly you should be able to get a 5V output from the +5V analog power terminal. Since you have turned the pot the voltage may have been changed and you need to use a DMM to measure the +5V output while turning the AVcc Adj pot until you get a 5V. Without a power supply connected you would get a full scale reading at all the ADC inputs.
You can use the same 24V DC for the PLC digital power supply.