General => Technical support => Topic started by: Hindsight on April 26, 2005, 08:55:02 AM
-
I'm using a T22H-NPN and am new to PLC programming. In my circuit when inputs 1 and 3 are both activated I need a timer that will activate output 1 for two seconds and then turn it off no matter how long inputs 1 and 3 are hot. A change in the status of inputs 1 and or 3 (loss of signal) would reset the timer so that if inputs 1 and 3 are activated again the timer would again activate output 1 for two seconds. Can you help an "old timer" learn a new trick?
-
The following should work. CR1 is any internal relay bit.
In1 In3 CR1
|------||---||--------+----(RLY)
| T1
+ ---(TIM)
CR1 T1 Out1
|------||---|/|--------------(OUT)
-
Worked like a charm!!! Thanks!