HI I have 1616+ ISTK
Got it communicating with the PC, OK, but cannot get the LCD to work. When trying to run the Clock or temperature demo program, all I get is the 2nd line and the 4th line on the LCD showing as solid blocks, I am sure it is a simple thing I am doing wrong. Can anyone advise !! ???
-
Try power cycle the PLC with the LCD plugged in. If it still doesn't work then you may have a damaged LCD or a bad LCD interface. Please contact the dealer or if you have purchased from us, contact sales@tri-plc.com to discuss about the cause of the problem.
Remember, the LCD is NOT hot-pluggable. So never plug/unplug the LCD into the PLC with the power on as that can damage the LCD display or the LCD driver interface on the PLC.
-
Power cycle gives same result. Will try new interface cable first. Thanks :)
-
Check and make sure your PLC is NOT in PAUSE mode.
-
OK thanks, how can I tell if the PLC is in pause mode, it seems to be running OK - is there a command to use for this ???
-
Make sure DIP-Switch #4 is not set to ON position. If DIP-Switch #4 is ON, it will set PLC to PAUSE mode. If the PAUSE red LED is lit/ON, then the PLC is in PAUSE mode. The PAUSE red LED is located near the PLC DC power connector.
Sincerely;
Albert Martinez
-
Thanks very much, I'll check this out and see what happens
:)
-
Your LCD could be faulty. If so, contact the dealer or us for a replacement.