I'm using a T100MD1616+ PLC for my project, among other functions i want to measure the rotation speed of a wheel (just as descriped in the user manual page 1-10).
I'm using an inductive sensor and the input works fine when i count the pulses normally.
When use the PMON, PULSEFREQUENCY commands nothing happes (not even an error code)
What can be wrong???
- pulse frequency range 0-200 Hz is that to slow?
Regards
Mikkel
-
Pulse measurement channel #1 maps to input #3, PM channel #2 maps to input #4.
You need to execute PMON 1 once only. Then connect your pulse signal to input #3, and whenever you execute
X = PULSEFREQUENCY(1)
the frequency of incoming pulses will be assigned to variable X.
The same goes for PMON 2 and PULSEFREQUENCY(2). However, remember that you should connect the pulses to input #4 in this case.
TBASIC is a generic language and PM1 and PM2 happen to share the same inputs terminals as input #3 and input #4 for T100MD+ PLC.
-
I've done what you described and it now works perfectly. ;D