I have a voltage input from -10V to 10V on my F1616 PLC. I only care about reading 0 to 10V. Can I just connect the input to the ADC directly, or do i need to eliminate the negative voltage via diode prior to connection to the ADC. I am concerned that the negative polarity might damage the ADC.
Please advice.
Thanks. :)
-
Negative voltage should not be applied to the PLC's analog inputs.
Although there are current-limiting resistors on the F1616-BA analog inputs to protect against temporary negative voltage spikes that could occur on the ADC inputs, prolong exposure may damage the ADC input.
If you add a diode to the input remember that there is a finite forward voltage drop across the diode and this should be compensated in your software.