General => Technical support => Topic started by: cch1955 on March 25, 2010, 09:28:06 AM
-
I am using this F2424 for the first time. The display is working fine but I am not seeing the keypad inputs when pressed using online monitoring. I am using the same key routine from your samples that I have used with the T100MD2424+.
I see no mention to the base address for the F2424 when using the MD-HMI Am I correct that it is the same as the T100MD2424+ ?
The zero key starts at input 25 and input 40 is the last input for the F4 key.
My program works fine in simulation, just not with the hardware.
Possibly I have a hardware problem with the keypad that does not effect the LCD?
Thanks
-
Did you plug in the 10 way connector into the Expansion socket (on the right edge of the PLC). It is a common tendency for F-series user to plug into the socket next to the LCD display. I know it may sound logical but that socket next to the LCD socket is reserved for future implementation of CANbus and is not currently used.
-
A simple solution. Another guy plugged in the cables and I did not notice the location.
I moved the cable and all works well.
Thanks for the prompt reply.