I am using an MD2424 as a master controller and using it to set and read varibles in eight MD888, using the hostlink commands with a RS485 loop and then they control the processes. But I have run in to a porblem were on of the slave MD888 will get bad data loaded into a varible which causes it's program to pause because of a data out of range alarm, if I reset the unit it starts to run again. Is there a command that the Master controller can send to the slave to cause a Master Reset in the slave unit when it can not communicate with the slave unit.
-
You can send the "CL" command to the slave to reset it.
Alternatively, in the slave PLC, add a circuit as follow:
RLY1
|-----||---------------[MaRST]
This way you can turn on RLY1 in the slave to cause it to reset itself.