Internet PLC Forum

General => Technical support => Topic started by: aphadke on March 26, 2007, 09:24:17 AM

Title: Problem transferring program to T100MD888+ from USB to RS232
Post by: aphadke on March 26, 2007, 09:24:17 AM
Hi,
        I have problem with transferring program to T100MD888+. I had no problem at initial connections. But when I connect to TLServer & hit IR* it says Warning: No resopnse from plc ! I am using USB to RS232 for transferring the program...but it works fine for another T100MD888+ I have. I checked the baud rate & tried to use the RS232 to RS232 port also but gives the same message....even I tired to pause plc & transfer the program....but hard luck... ???

Plz help me out..
Thx
Atul
Title: Re:Problem transferring program to T100MD888+ from USB to RS232
Post by: support on March 26, 2007, 08:16:47 PM
If the same program and RS232 convert works on one PLC but does not work on another one, and turning on DIP switch #4 and reset the PLC and you still can't communicate with it using 9600 bps, then it is likely that the board's RS232 port may have failed. please email to: support@tri-plc.com for an RMA # and arrange for return to the dealer for service/repair.